IAS in "Initializing" mode and fails to get past this on the LCD screen. Intrusion Alarm System (IAS) also referred to as the OP5 or Remote Arming Terminal RAT

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • IAS in "Initializing" mode and fails to get past this on the LCD screen. Intrusion Alarm System (IAS) also referred to as the...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • sesa139513
    sesa139513

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2326 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

IAS in "Initializing" mode and fails to get past this on the LCD screen. Intrusion Alarm System (IAS) also referred to as the OP5 or Remote Arming Terminal RAT

Picard Product_Support
‎2018-09-07 08:53 PM

Issue

IAS stands for Intrusion Alarm System. If stopped in "Initializing" then follow these steps. Normally if using the bin file from I/NET version 2.21, the display will show correctly. The bin file for version 2.30 and above may have to complete the step to get past the initializing screen.

Intrusion Alarm System (IAS) also referred to as the OP5 or Remote Arming Terminal RAT

Environment

I/NET Seven with a 7798C and Intrusion Alarm System

I/NET version 2.21 and above. I/NET version 2.16 and bellow do not support the OP5 Terminal.

Cause

Configuration Settings and database download. Normally if using the bin file from I/NET version 2.21, the display will show correctly. The bin file for version 2.30 and above may have to complete the step to get past the initializing screen.

Resolution

After a software download from I/NET Seven 2.30 to current, the OP5 is always in Initializing Mode.  Hot to correct this?

  1. In the MCU Configuration Editor, the type has to be DPU
  2. The device has to be saved in Network Configuration

If these two are true, it will pass the initialization part of initializing mode.


Here are the steps in order to get the OP5 terminal to setup at my desk: 

Set the OP5 as link 29
Backup the existing database.
If DCU password is requested, it is 4444
  1. Backup existing database.
  2. Copy the Database from CD\support\IAS Templates\8_Zones to local hard drive
  3. Copy the SAV file from CD\support\IAS Templates\8_Zones to local hard drive in the Sav folder of I/Net. Be sure to rename DCUxxxx.sav
  4. Restore database you just copied from CD
  5. Go into Network Configuration and delete link 94
  6. Go into Network Configuration and save the link penetrating down all levels
  7. Do a station restore from the SAV file you copied to the 7798 and renamed from CD. I recommend SLI then DPU, in that order.
  8. Go into Edit, Controller, MCU Configuration and make OP5 29 link DPU
  9. Go to Edit -  Controller - Intrusion Alarm System
  10. Add point OP5 - 2 (This one is configured to link 29), Choose one or all if so desired. Click OK twice.
  11. The led light in the upper left corner on the OP5 will be lit now. Make a station restore and the OP5 keypad appears.
  12. Go into pull down menu for Access
  13. Add Door to Tenant
  14. Add Door Schedule for all three groups
  15. Go into MCU Config and check OP5 is on Link 29, and set for DPU
  16. If OP5 is still ‘Initializing’ then change MCU Config Link 29 to Internal, exit
  17. Go into MCU Config and change Link 29 to DPU

My OP5 works using I/Net 2.40, Xenta 527, 7798C, OP5. I have the OP5 link as 29. Please alter the instructions to fit your link number. Step 6 refers to the link 94, which is part of the database here, you can delete since it is not relevant to your location. Here is a pdf with an example of the setup of a typical OP5.

Another paper written on the steps they performed using the OP5 is found Here.

Labels (1)
Labels:
  • TAC INET
Attachments
Tags (1)
  • Find more articles tagged with:
  • 4911
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.