Issue
In the IAC400 and IAC600, a digital output cannot be forced to a different value.
Product Line
EcoStruxure Building Operation, Satchwell MicroNet
Environment
- IAC400
- IAC600
- SBO
Cause
When an IAC400 or IAC600 is imported into SBO using the Micronet interface, on a digital output, the output cannot be forced to another value.
Resolution
- In Visisat, create the SBO export file.
- Before using the 'Data Import' into the Micronet Interface in SBO, locate and open the export XML file with a suitable program, e.g. Notepad++.
- Locate the respective controller's 'Digital Output Override State' with the line <P1="IsNonVolatile".... (Note: if opened in another application, e.g. Internet Explorer, the word order may be different!)
- Change Value= "1" to Value="0"
Note: IAC420s are unaffected