Issue
The address of the IAC touch screen will reset to default (65) on Sundays when time broadcast is used
Product Line
EcoStruxure Building Operation, Satchwell MicroNet
Environment
- Building Operation Enterprise Server
- Building Operation Automation Server
- MicroNet transition
- IAC touch screen
Cause
When the time broadcast on an AS or ES MicroNet interface the address of the touch screen will reset
Instead of broadcasting the day number as a 7, the day number is sent as a 0.
The IAC touch screen does not understand day 0, resulting in the touch screen resetting to defaults. No other days are affected.
When the touch screen resets, the touch screen's address is also reset and defaults to address 65.
Unless the touch screen was originally configured as address 65, the controllers on the SubLAN of the touch screen will not be available, until the correct address is entered into the touch screen.
Resolution
A hotfix is available from Product Support for SBO version 1.7.1.12604
This correction has been included in SBO 1.8 and later releases.
Earlier SBO version will need to be upgraded to SBO 1.7.1 with the hotfix applied or upgrade to version 1.8 when available