I2V graphic conversion has unpredictable results
  • I2V graphic conversion has unpredictable results
  • sesa139513
    sesa139513
  • SESA116857
    SESA116857
‎2018-09-06 02:59 PM
I/NET Site
Sometimes the graphics being generated by the I2V conversion do not seem to match the original I/NET graphic pages or include additional graphic items or the size and position of the recognizable I/NET page is significantly different. These problems are typically caused by hidden items in the I/NET graphic page.
To verify if this is the case open the I/NET graphic page in the I/NET editor and use the View-Page Properties option to change the page size. By increasing the page size to 4 times the current values you should be able to see if any of the unexpected items are present. If these object should not be in the graphic then you can delete them and then reconvert the graphic page after returning the page size to normal.