Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

I/Net - What is an acceptable induced voltage on to I/Net signal terminals

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/Net - What is an acceptable induced voltage on to I/Net signal terminals
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa150561
    sesa150561
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1169 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/Net - What is an acceptable induced voltage on to I/Net signal terminals

Picard Product_Support
‎2018-09-06 10:44 AM

Issue

  • What is an acceptable induced voltage on to I/Net signal terminals

Environment

  • I/net
  • SCU

Cause

If you have 10V which is induced on to an input cable. And The installer ran
24Vac alongside signal wires in a multicore cable with a common screen. And  have a plan to eliminate the induced voltage by reducing the number
of pairs carrying voltage and using other cables

Resolution

Of the input signal types, the Thermistor type is considered the most vulnerable to the pickup of stray voltage from sources in the local area. This is because the AI input is a high input impedance (as it is with all voltage measurement modes of operation), AND the signal source is also very high impedance (the 10K thermistor itself). With one side of the circuit grounded, this presents the 10K ohm impedance of the signal wire as a prime candidate for inducing AC voltage noise from and local adjacent AC voltage sources AND especially any such run in the same cable.

There is no “acceptable limit” definition on such AC pickup.
Acceptability is directly related to the system application and/or customer tolerance for fluctuations of temperature readings.

In the room temperature range, a thermistor signal changes by only ~ 54mv for each degree C.
Without filtering, this 54mv/C sensitivity would produce constant variation form small induced noise levels.

We provide both hardware and software filtering on the analog signals that allows rejection of AC noise seen on the input terminal, BUT you still want to minimize the level of the noise pickup as seen on the analog inputs.

In the I/NET controllers the hardware filter provides a 94/95 % reduction of the 50/60 hz AC noise level presented to the controller. The controller firmware follows with implementation of  deglitching and averaging filters that further reduce the effect of noise on the AI point value.  We also have a input filter technique specifically targeted at reducing the impact from AC line induced noise. That filter works on the principle of making the AI readings at a scan rate of 1.5 times the AC line frequency. This is the purpose of making the AC line frequency a configuration item (50 or 60 hz) in the CLAN controllers. On the SubLAN, this is scan rate is fixed at 25ms (1.5 times 60hz) which make the line frequency filter not as effective for 50hz, but still very helpful.   As the analog inputs are scanned, we capture a reading on the negative or positive cycle of the induced noise and then we average that with a reading taken from the opposing cycle of the induced AC noise as seen 25ms (or 20ms) away from the previous sample. The average of the positive and negative cycle of the induced noise creates a near complete cancelation of the induced error – for a sinusoidal wave noise signal. This technique does a great job of producing a notch filter centered on the AC line frequency and reducing/filtering the impact from such line frequency noise.   This combination of several filters allows you to see AC line induced noise on the analog input terminal, and still maintain a stable temperature reading in many cases.  Note -- If the AC noise is non-sinusoidal, due to anomalies in the noise transfer or originating from an AC source other than the sine wave AC power line, then the affectivity of the noise reduction will be reduced and signal reading impact will be larger.

The 10V of induced voltage you describe is very large (huge) and far beyond anything I have seen, but then I have never seen 24VAC wired in the same cable with thermistor signals.  Separation of the 24VAC as you describe below is needed.

Your described past tolerance for  5V is also above what I would expect to accept.  

However, it is possible that the AC line frequency filter has been making such high noise level appear acceptable on the temperature reading display.  

For possible work-around use, the high impedance of the thermistor source makes the addition of a capacitor on the AI terminal to ground very effective in reducing the applied voltage from AC noise pickup. Here a capacitor value in the range from 2 to possibly 100 micro-farads can sometimes be useful to reduce or work-around an installation wiring problem. The capacitor should be of the “Low Leakage” type.  Leakage in the capacitor would be exhibited as a small reduction in the DC voltage and associated increase in the temperature reading.  The higher the micro-farad capacitance value, the more reduction in noise you will achieve, but it is easier to obtain low leakage capacitors in the smaller capacitance values.  If polarized electrolytic capacitors are used, be sure to position the negative terminal toward ground.

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 12211
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of