Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

I/NET to Building Operation Bindings

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/NET to Building Operation Bindings
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Chris_Asbury
    Chris_Asbury
  • sesa139513
    sesa139513
  • Tom_Poovey
    Tom_Poovey
  • Derrick_Ratliff
    Derrick_Ratliff
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1393 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/NET to Building Operation Bindings

Picard Product_Support
‎2018-09-06 09:52 AM

Issue

Trouble with I/NET to Building Operation bindings.

Site can bind an internal I/Net AO to a analogue value in Building Operation but the value won't update.

Value appears with a blue triangle that says "unresolved". 

Environment

I/NET Seven together with StruxureWare Building Operation

Cause

I/NET points are integrated into Building Operation as points. When you upload the device configuration to the Enterprise Server, the configuration and point information are created in the System Tree pane. You edit and command the points as needed, using WorkStation and I/NET Seven editors.

There are ten possible point types available in I/NET:

  • Analog input (AI)
  • Analog output (AO)
  • Discrete input (DI)
  • Discrete output (DO)
  • Discrete alarm (DA)
  • Discrete monitor (DM)
  • Discrete control (DC)
  • Digital input (GI)
  • Digital output (GO)
  • Pulsed input (PI)

Resolution

For any I/NET inputs (AI, DI, DM, GI and PI) it is only possible for operator changes to be made via the Building Operation Properties. It is not possible to programmatically control I/NET inputs and therefore not to be able to bind an output to an I/NET input point. It is also not possible to programmatically change any points Test state, any outputs (AO, DC, DO and GO) Manual state. And finally it is not possible to programmatically acknowledge an alarm. Therefore it is not possible to bind any script, schedule, FB, etc to any I/NET Points Test, Manual, Alarm Acknowledge or input point.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 15006
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of