I/NET SubLAN communication best practices

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/NET SubLAN communication best practices
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1712 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/NET SubLAN communication best practices

Picard Product_Support
‎2018-09-07 02:41 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-11-02 06:33 AM

Issue

  • How do the 7793 and 7798 handle retries? 
  • Improving I/NET sublan communications
  • Excessive MCU Lost messages in AMT
  • Command Error messages in AMT

Product Line

TAC INET

Environment

  • I/NET sublan
  • 7793, 7798

Cause

If there are issues on the physical layer of the network, this will effect the reliability of I/NET communications. However, these risks can be lessened with some best practices.

Resolution

Best Practices and Troubleshooting measures to improve sublan communications:

  • Ground the 24V line coming into MRs and ASCs
  • Connect ground to the earth ground terminal of DPUs and SCUs.
  • Bond the shield of the LAN cable all the way through the network, not landing it on any controller anywhere and then tie it to earth ground in one location. (see diagram)

INET Sublan.jpg

 

SubLAN Communication Explained:

  • The first packet to any sublan device goes out on the primary channel, terminals 1 and 2 of the sublan connector on the 93/98.
  • If the device doesn't respond in time, a second packet is sent out on the alternate channel, terminals 4 and 5.
  • If there is still no reply, a third packet goes out on the primary
  • Finally, if there is still no reply, that device is marked as lost which generates an "MCU Lost" message.

Optional Configuration for only using Terminals 1 and 2:

  •  If you are using only Terminals 1 and 2 you could be missing 33% of it's retry capacity. If you follow wiring guides and best practices the device will answer on the first packet every time, however if you have not followed the guide all it takes is a little noise to make the retries necessary.
  • If you are unable to use a loop configuration, or want to avoid the extra potential for noise and EMI, in stall a jumper on the sublan connector from terminal 1 to 4 and from terminal 2 to 5
  • The allows you to get the extra retry, without the extra cable
  • This will also function if you have some controllers on channel A and some on Channel B
  • The SLI doesn’t have to be at the end of line on sublan communication

INET Sublan_optional.jpg

 

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 3510
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of