Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

I/NET Seven with SQL 2008

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/NET Seven with SQL 2008
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4507 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/NET Seven with SQL 2008

Product_Support
‎2018-09-07 10:58 AM

Last Updated: RobertAndriolo Champion ‎2026-07-07 05:00 PM

Issue

  • Receive "Initialization error" when trying to start I/NET with SQL 2008
  • When we installing SQL Server 2008 Standard for I/NET Filemaster, what are the main components we should include?
  • When editing / adding a new I/NET Configuration Profile the Database Server section is blank
  • DBCreate does not start.  Appears in task Manager but no user interface is shown.
  • Within DBCreate the restore option is grayed out

Product Line

TAC INET

Environment

  • I/NET Seven 2.4x
  • Microsoft Windows Server 2003, Windows XP, Windows Vista, and Windows 7/10 families of operating systems. (both 32 and 64 bit)
  • Microsoft SQL 2008 Standard or Express Editions
  • Microsoft SQL 2008 R2 Standard or Express Editions

Cause

I/NET must have the SQL 2005 Backward compatibility file installed.  If this is not installed I/NET will not locate the SQL Server and hence will issue an “initialization failure” error.  This is can also be identified in either the DBCreate or I/NET Configuration application editors which will show no entries in their "Database Server" settings.

The document also details information that is necessary for a Standard or Express editions of SQL 2008 / SQL 2008 R2.

Resolution

Follow the instructions below extracted from the document called "SQL2008 Expr Install Inst.pdf".  This document is found on I/NET Seven CD under the 'SQLExpress' folder.  For SQL 2008 R2 installations refer to the following document SQL2008 R2 Expr Install.pdf, also found in this same folder . 

Installing SQL Server 2005 Backward Compatibility

SQL Server 2005 backward compatibility must be installed for SQL 2008.

To install SQL Server 2005 Backward Compatibility

  1. Navigate to the SQLBcm directory on the TAC I/NET Seven installation CD.
  2. Launch the SQLServer2005_BC.msi file.
  3. Follow the prompts on each screen and accept all defaults.
  4. After the install check the SQL Server Services
    1. SQL Server Browser is RUNNING
    2. SQL Server (MSSQLSERVER) is RUNNING
  5. Check the SQL Server Network Configuration Protocols
    1. Enable Named Pipes
    2. Enable TCP/IP

Completing the Installation

Proceed with the installation of TAC I/NET Seven on your PC. For installation instructions, refer to TCON298, TAC I/NET Seven Getting Started.

Note: Run Inetcfg.exe before starting TAC I/NET Seven for the first time.

This is necessary to attach TAC I/NET Seven to the database and avoid an “Initialization failure” error.

Note: Before file equalization will operate, the system must be rebooted or the INETEQZMERGE service must be manually started.

 

Also refer to Installing I/NET 2.42 or higher and Vista 5.1.7 or higher on a 64-bit operating system for additional details on installing I/NET with SQL 2008 R2.

Labels (1)
Labels:
  • TAC INET
Attachments
Tags (5)
  • Find more articles tagged with:
  • 2.40
  • 2.41
  • 2.42
  • 2.43
  • RobertAndriolo26
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore