Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

I/NET Reference Host Suggested Configuration

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/NET Reference Host Suggested Configuration
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1386 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/NET Reference Host Suggested Configuration

Picard Product_Support
‎2018-09-06 01:38 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:48 AM

Issue

I/NET Reference Host Suggested Configuration

Environment

  • I/NET
  • NPR
  • Xenta 527-NPR
  • Xenta 527
  • Xenta 913
  • Xenta 731

Cause

There are many opinions about the correct use of Reference Hosts.  This is a suggested use which will be successful for most sites.

Resolution

 From TCON 298

A Reference Host is any TAC I/NET workstation, NPR, or Xenta 527/527-NPR that will serve as a source of IP addresses. Any of these devices attached to an Ethernet LAN can be used as a Reference Host. 

Each time I/O Server is started on a workstation, it provides the workstation’s IP address to each remote host designated as a Reference Host. I/O Server also requests and receives a list of all host IP addresses that are known to the remote host at that time. I/O Server must be running on the remote host for this address exchange to occur. I/O Server compiles and maintains a list of all the remote hosts that it learns about. Ultimately, all hosts in the network will know the IP addresses of all the other hosts.

 Ideally, you should determine 1 or at most 2 devices to serve as your Reference Host.  This device would ideally be a Xenta Server or an NPR, but a Host workstation that has I/O Server running 100% of the time will work as well.  

All devices on the system will use this as a single Reference Host. No others are needed.  When the device comes online it will contact the Reference Host and get the site’s Routing Table.  The Reference Host can have an empty routing table. 

Once the Routing Table is shared, Reference Hosts are no longer needed.  You can leave the single entry in place. This will allow a quick recover, in the event of a critical system failure. 

Here are a few reasons for using multiple Reference Hosts:

  • Temporarily add a new device as a Reference Host on the Sites Reference Host or a workstation to aid in bringing it online
  • A large site may desire to have 2 Reference Hosts in case one is offline when a device comes online.
  • An  I/NET site that spans multiple locations may wish to declare a local Reference Host for each building and a network Reference Host
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 5672
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore