Issue
DDC Control Override
MR Control Override
Environment
I/NET
MR-AHU
7718 7716 7756 7798 7793
Cause
A control is needed to override the standard control for a point. Possibilities include using an ASC point for a different purpose.
Resolution
The most effective means to program an over-ride all logic is to use an Event Sequence containing the with Lock element. This will over-ride anything other than a point in manual control.
Please see Appendix A "DCU Control Hierarchy" from TCON300 for complete Control Hierarchy.