Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

I/A Series R2 station idle time is too low. How do I correct it?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A Series R2 station idle time is too low. How do I correct it?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1090 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A Series R2 station idle time is too low. How do I correct it?

Picard Product_Support
‎2018-09-10 12:44 PM

Issue

My I/A Series R2 UNC station idle time is about 5%.  How do I improve it?

Environment

I/A Series R2 UNC (410, 500, 510, 520, 600, 610)

Cause

Station processing was not optimized to maximize the processor idle time.

Resolution

  1. Run the System Spy by entering http://:3011/system/spy into browser and specifying the IPAddress of the UNC.
  2. When the display comes up, scroll to the bottom of the page and click the 'Reset Counters' link.
  3. Wait 45 seconds for the counters to be updated before clicking the link to return to the spy statistics screen.
  4. Note the displayed idle time.  If it is above 20% no further action is required.  If below 20%, continue with the steps below to optimize the timing.  Please be aware that these steps are only suggestions.
     
  5. Increase the cycleTime on the UIEngine Service properties--config screen from the default of 500 ms to a value in the range of 2500 to 5000 ms.  This value controls the update frequency of point values on the WorkplacePro and Graphic screens, both locally and via web browser access.  This timing affects the update rate for points on graphic screens.  Remember that regardless of how fast the update rate is specified, updates will only occur when new values are received from point or device.
  6. All LOG objects that have a log interval of greater than 2 minutes should be configured with an execution frequency of "minutely".  In addition, any objects being logged or used in calculations for a logged value, if not being used for other purposes, should be configured for "minutely" execution.
  7. Any objects that are involved with passing or using low priority values such as outdoor air temperature/humidify (and using/passing any other low priority value objects) should be assigned an execution frequency of "slower".
  8. Verify that there are no "custom program" objects that could be replaced with standard objects or combinations of standard objects.  In any case where the station contains more than the recommended maximum number of program objects, an effort should be made to reduce the number of program objects by as much as possible.
  9. Repeat steps 2, 3 & 4, above.  If the idle time is still less than 20% continue with the steps below to optimize the execution frequency time intervals.
     
  10. Review status screen for the Control Engine service noting the following four sets of corresponding values.
  11.  If any of the four "Overruns" counters shows a significant number of overruns, note this fact for use in step 15 below.
  12. Compare each of the four "...AverageExecuteTime" values to the corresponding execution frequency value (on config tab) and if the value exceeds 50% of the configured execution frequency note this for use in the step 14.
  13. Open the Config tab of the ControlEngineService Properties screen.
  14. Referring to the values noted in step 12, the "normal" execution frequency needs to be set to a time value that is at least double the value of the "normalAverageExecuteTime".  If this time value exceeds the setting for the "slower" execution frequency, the "slower" execution frequency should be increased so that it is at least 50% greater than the "normal" execution frequency.  Adjust the fastest and faster executionFrequencies proportionally to the change made in the normal execution frequency.  For example if the "normal" execution frequency was increased from 2 to 5 seconds, the "fastest" execution timer would be increased to 1.3 sec and the "faster" execution timer increased to 3 seconds. 
  15. If any corresponding "overruns" counter shows a significant percent of overruns, as compared to the corresponding cycle counter, and you did not already increase the corresponding execution frequency to at least double its original setting, increase it appropriately.  Refer to step 14, above, regarding the suggested changes for the other execution frequencies.
  16. Apply the settings, save the station and restart it to force the changes to become effective.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 11017
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of