I/A Series R2 programLib jar FlexAnalog object does not pass NaN
  • I/A Series R2 programLib jar FlexAnalog object does not pass NaN
  • Kim_Baze
    Kim_Baze
  • WaynePeters
    WaynePeters
‎2018-09-06 10:53 AM
The FlexAnalog object in the I/A Series R2 programLib jar does not pass the NaN (not a number) to the link when the value at the FlexAnalog input is changed from a valid value to NaN.
TAC IA Series
I/A Series R2
The object was based off the standard Analog Input object where the object holds the last valid value when NaN is applied to the input.
There is a jar available that has an updated FlexAnalog object that will pass the NaN to the link when the value at the FlexAnalog input is changed from a valid value to NaN (not a number).  Contact Product Support Services to obtain this jar.
  • TAC IA Series
Tags (9)
  • 11758
  • emb
  • goes
  • nremodules
  • provide
  • pss
  • same
  • should
  • v523t