I/A Series R2 Optimum Start Stop program object may improperly calculate start time when outdoor air temperature compensation is used.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A Series R2 Optimum Start Stop program object may improperly calculate start time when outdoor air temperature compensation...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1658 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A Series R2 Optimum Start Stop program object may improperly calculate start time when outdoor air temperature compensation is used.

Picard Product_Support
‎2018-09-11 01:30 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:47 AM

Issue

I/A Series R2 Optimum Start Stop program object may improperly calculate start time when outdoor air temperature compensation is used.

Environment

I/A Series R2 (all versions)

Cause

Optimum start / stop compensation is performed through the use of a program object. The object could calculate a negative start lead time when outdoor air temperature compensation was used.

Resolution

A check was added to the program object to prevent a calculated negative start leadTime due to outdoor air temperature compensation.  The revised object is available for download from The Exchange Download Center. Download the file >> OSS for Niagara 08_03_11.zip

In addition, the object includes the following change history.

10-Nov-00  Moved the parameter reset control to an external stimulus

16-Aug-01  Changed reset input from BooleanPriority to DateTime

20-Dec-02  Added check for command time > next event time to account for a large leadtime calculation that results in a start time prior to midnight

14-Sep-05  Added safety check to prevent dynamically adjusted runtime factors from becoming too large

25-Apr-06  Corrected the following stop-time issues:
           1) stop-time calculation when earliestStopTime is after schedule stop time
           2) stop-time calculation when start/stop times span midnight
           3) determining when to perform stop-time analysis
  
05-Nov-08  Added changes from 2002 and 2003
           Added prestart (maxStartLimits) and comfortLimit inputs 18 Nov 02
           Added the ability to use OA temperature for OSS calculation 24 Feb 03

12-Dec-08  Added OA temperature to message strings.  Added output for calculated command time.

19-Feb-09  Corrected issues with stop-time analysis:
           1) lastStartTime was being used for stop-time calculation
           2) analysis for heating was adjusting drift time for cooling
           3) analysis for cooling was adjusting drift time for heating

           Corrected issues with stop time calculation:
           1) heating mode failed to drift when > upper comfort limit
           2) cooling mode failed to drift when < lower comfort limit
           3) stop mode calculation always reflected the next event time

15-Oct-09  Added properties and check to prevent dynamically adjusted drift time factors from exceeding a specified maximum value.

03-Aug-11  Added check to prevent calculated negative start leadTime due to outdoor air temperature compensation.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 7863
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore