I/A Series R2 LON Device Manager does not allow me to perform a "Replace Node" to replace an MNL standard controller with a newer version of the same controller.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A Series R2 LON Device Manager does not allow me to perform a "Replace Node" to replace an MNL standard controller with a n...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • WaynePeters
    WaynePeters

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1407 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A Series R2 LON Device Manager does not allow me to perform a "Replace Node" to replace an MNL standard controller with a newer version of the same controller.

Picard Product_Support
‎2018-09-10 03:26 AM

Issue

I/A Series R2 LON Device Manager does not allow me to perform a "Replace Node" to replace an MNL standard controller with a newer version of the same controller.  For example, replacing MNL-20RS1 with MNL-20RS3.

  • MNL-xxRF2 replaced by MNL-xxRF3
  • MNL-xxRH2 replaced by MNL-xxRH3
  • MNL-xxRR2 replaced by MNL-xxRR3
  • MNL-xxRS1 replaced by MNL-xxRS3
  • MNL-xxRS2 replaced by MNL-xxRS4
  • MNL-xxRV2 replaced by MNL-xxRV3

Environment

I/A Series R2, UNC-410, UNC-520

Cause

Slight changes to the profile were made requiring a change in the device's program ID. The replace node will only succeed if the device program IDs exactly match.

Resolution

There are three methods to exchange the MNL shadow objects (e.g. MNLRS1 to MNLRS3, etc.).  The first method is to manually use WorkPlace Pro to delete the existing shadow, adding the new shadow object, and re-linking the associated logic.

The second method is to manually edit an updated XML backup of the station database.  The following summarizes the changes required to convert a shadow object from V3.x controller profile to V4.x controller profile via XML. It is recommended to use an editor such as Textpad which is available at no cost and can be downloaded at http://www.textpad.com.

Fan Coil Profile MNLRF2 replaced with MNLRF3
Heat Pump Profile MNLRH2 replaced with MNLRH3
Rooftop Profile MNLRR2 replaced with MNLRR3
Satellite Profile MNLRS1 replaced with MNLRS3
Satellite Profile MNLRS2 replaced with MNLRS4
VAV Profile MNLRV2 replaced with MNLRV3

The same modifications were made between the various profiles so the following can be used to modify each.

Step 1: Replace the shadow object referenced in the text file with the appropriate new object. Do not modify the node name. For this example, replace MNLRS1 with MNLRS3.

 

 

Step 2: The nvoSecAlarm has been replaced by nvoDeviceAlarm. The only change was to remove the Sec (Siebe Environmental Controls) reference and make the nvo more generic in name. All other information (i.e. SNVT type, etc.) remains completely unchanged. Since the nvo was specifically designed to work with these devices, a binding will most likely not exist.  Note: There are two tags to edit, one tag at the start of the definition and one tag that ends the definition.

Step 2: The nciSecModelNum has been replaced by nvoDeviceInfo. The network configuration property was removed to free precious EEPROM required to compile the new Echelon library. The SNVT type and index position remains unchanged. This nci was a manufacturer defined property and typically only read by the user. The information now is calculated and provided as an nvo. Replace the entire section.

The third method is to use a utility included with the Smartware Tech WorkPlace Pro Utilities package.  A utility named “Profile Update” can be used to work on an offline XML to upgrade these objects. Additional information as well as Smartware's contact information can be found at http://www.smartwaretech.com.

 

 

 

 

 

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 6281
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of