I/A Series R2 (AX) Tunneling does not work in Windows 7
  • I/A Series R2 (AX) Tunneling does not work in Windows 7
  • sesa116871
    sesa116871
‎2018-09-11 06:28 AM
The Niagara Tunnel service in Windows 7 indicates that it is started; however the tunnel window will not pop-up
Niagara R2 version 5.35, Windows 7 32-bit.
The Interactive Services Detection service is disabled. This service must be enabled for the tunnel client to work.
Verify that Interactive Services Detection is started.  Set the service to automatic, start it, and re-boot the computer.
  • TAC IA Series
  • 15862