I/A Series (Niagara) R2 UNC won't boot after downgrading system software to a version earlier than release 529

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A Series (Niagara) R2 UNC won't boot after downgrading system software to a version earlier than release 529
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1770 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A Series (Niagara) R2 UNC won't boot after downgrading system software to a version earlier than release 529

Picard Product_Support
‎2018-09-07 02:07 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:47 AM

Issue

After using the I/A Series (Niagara) R2 Admin Tool Installation Wizard "Upgrade" process to install an earlier version of the R2 OS and NRE, the UNC will no longer reboot properly. The heartbeat LED remains turns on and stays on. The software was downgraded to a release earlier than R2.301.527.

While watching the bootup process on a serial console connection, the bootup log shows the following message just before the UNC reboots:

old clock frequency detected, modifying and rebooting
->

Since the BOOT Flash chip does not allow its clock frequency to be changed, this "change, reboot, start, clock change, reboot" process will continue as long as the UNC is powered.

Product Line

TAC IA Series

Environment

  • UNC-410 with serial number 36218b and newer
  • UNC-520 with serial number 36184b and newer

Cause

The UNC features a new bootflash chip that is incompatible with the older releases of the R2 software.

When the affected UNCs are shipped by the factory the following yellow warning label is attached to the transformer cover:

WARNING!

This Universal Network Controller (UNC)
features a new bootflash chip. To properly
configure or install the software you MUST
use one of the following releases.

Release R2.301.527 or newer

Failure to follow these instructions will cause
the UNC to become inoperative.

Refer to Product Announcement PA-00123 on The Exchange Download Center for more details.

Resolution

Contact Product Support to obtain a return authorization number. The UNC returned with this issue will be repaired by the factory for a nominal fee of $250.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 4876
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore