I/A Series (Niagara) G3 ENS (Enterprise Network Server) upgrade Procedure
  • I/A Series (Niagara) G3 ENS (Enterprise Network Server) upgrade Procedure
  • sesa116868
    sesa116868
‎2018-09-06 02:05 PM
What is the procedure to upgrade an existing I/A Series Enterprise Network Server to a newer release of the G3 software?
Existing I/A Series G3 ENS installation.
Newer release of the G3 software to be installed.
Upgrade
  1. Back up existing ENS station.
  2. Open the Application Director in the existing version of WorkBench and stop the running station then close Workbench.
  3. Install new release of the I/A Series G3 software by running the setup.exe program from the distribution file set (expanded zip file or CD).
  4. If the installer prompts to allow copying of settings from previous installation, allow the copy to proceed.
  5. At the end of the installation process, allow the installer to start the new Niagara Daemon but not Workbench.
  6. Under the Stations folder in the old installation of the G3 software, locate the folder for the station that was being run.
  7. Copy the entire folder locate in step 5 from the Stations folder of the old installation to the Stations folder of the new installation.
  8. Start the new version of the Workbench, then use the Application Director to start the copied station.
  • TAC IA Series
  • 4695