I/A Series Niagara 4.8 or later Upgrade and JACE 8000 Memory Requirements

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A Series Niagara 4.8 or later Upgrade and JACE 8000 Memory Requirements
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • WaynePeters
    WaynePeters

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3598 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A Series Niagara 4.8 or later Upgrade and JACE 8000 Memory Requirements

Lt. Commander WaynePeters Lt. Commander
‎2019-09-18 05:35 AM

Last Updated: Guinan RandyDavis Guinan ‎2020-07-27 10:02 AM

Issue

Unable to upgrade a JACE 8000 to I/A Series Niagara 4.8 or later due to insufficient memory allocation.

Product Line

TAC IA Series

Environment

  • I/A Series Niagara 4
  • I/A Series JACE 8000

Cause

I/A Series Niagara 4.8 or later running on a JACE 8000 will consume approximately 40 MB more memory than Niagara 4.7 due to new features including a new OS (operating system) and JRE (Java Runtime Engine).

Resolution

The following information will help identify if there is sufficient system memory to upgrade to Niagara 4.8 or later and if not, how to tune memory parameters to increase required system memory. Use the following analysis to determine if a Niagara 4 platform, operating at release 4.7 or earlier, requires a memory allocation adjustment PRIOR to upgrading to version 4.8 or later.

  1. Determine the amount of Free Physical RAM in the embedded platform while running the current release (prior to a 4.8 or later firmware upgrade)
    1. Open the embedded platform with the Niagara Platform Administrator tools.
    2. Check the amount of Free Physical RAM that is currently available. The image below displays where the information is located.Image1.jpg
    3. If the amount of Free Physical RAM is greater than 40,000 KB (40 MB), the JACE 8000 platform is ready to perform an upgrade to Niagara version 4.8.  If the amount of Free Physical RAM is less than 40,000 KB (40 MB), the platform will require adjustment to the NRE Memory allocation using the steps below.

  2. Determine the amount of memory allocation required
    1. Subtract the current amount Free Physical RAM (MB) from the required 40 MB allocation. In the example above, 40 MB – 26.3 MB = 13.7 MB. Round this value up 14 MB.
    2. Next, add a buffer value of 10 MB to the previous result for a new total of 24 MB.
    3. System memory will be freed by reducing size of RAM disk used for histories. Ensure that /mnt/aram0 contains at least this “allocation adjustment” free space.  Using the above example, there is 326,944 KB (approximately 326 MB) of available memory that can be re-allocated to satisfy the additional 24 MB requirement.  Note: If there is not enough free space available in the /mnt/aram0, please contact Product Support for more options.

  3. Adjust the NRE Memory allocation
    1. Use the Platform Administrator tool to locate and select the Configure NRE Memory button as shown below.Image2.png
    2. Record the current memory allocations for Heap Space and Meta Space by reviewing the memory sizes shown below.Image3.jpg
    3. Increase the Meta Space by using the Meta Space slider to provide additional working space. Slide the Meta Space adjustment shown below to add 40 MB to the existing value of 48 MB increasing the Meta Space to 88 MB.Image4.png
    4. Increase the System Reserve by the required 24 MB calculated in the example above. Slide the System Reserve adjustment shown below to set the value to 24 MB.Image5.png
    5. Return (increase) the Heap Space back to the original 384 MB size by adjusting the Heap Space slider shown below.Image6.png
    6. The final adjustment will bring the Meta Space back the original 48 MB size by adjusting the Meta Space slider shown below.Image7.png
  4. Save the changes and reboot the JACE 8000.  Using the information from Step 1, verify that the Free Physical RAM is now above 40 MB.  If confirmed, the JACE 8000 platform is ready to perform an upgrade to I/A Series Niagara version 4.8 or later.
Labels (1)
Labels:
  • TAC IA Series
Tags (6)
  • Find more articles tagged with:
  • Jace 8000
  • N4.8
  • N4.9
  • RandyDavis20
  • upgrade
  • WaynePeters19
Was this article helpful? Yes No
100% helpful (4/4)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore