Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

I/A Series MNL-VAV controller displays a small air flow value when no airflow is present

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A Series MNL-VAV controller displays a small air flow value when no airflow is present
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • WaynePeters
    WaynePeters

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2277 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A Series MNL-VAV controller displays a small air flow value when no airflow is present

Picard Product_Support
‎2018-09-11 12:51 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-08-14 06:55 AM

Issue

I/A Series MNL-VAV controller continues to display a small air flow value (CFM or L/S) even when airflow is not present (zero flow conditions). This condition is typically seen as small CFM readings on graphics screens when air is not present (AHU off condition).

Product Line

TAC IA Series

Environment

MNL-V1RV3-2, MNL-V2RV3-2, or MNL-V3RV3

Cause

The I/A Series MNL-V1, V2, V3 and controller platforms were recently redesigned to incorporate the latest Echelon FT 5000 Neuron Smart transceiver. With no air flow, when the fan system is not running, minor fluctuations in duct pressure could result in false air flow readings from the MNL-V1RV3-2, MNL-V2RV3-2, and MNL-V3RV3.

Resolution

Use the MNL Firmware Updater Utility to update the MNL-V1RV3-2, MNL-V2RV3-2, or MNL-V3RV3 controller firmware to version 4.3B5. A velocity pressure reading below 0.005 in. WC (1.25 Pa) will be processed within the controller as no or zero flow. Controllers within these date code ranges should be updated with the utility detailed below.

  • MNL-V1 and MNL-V3 starting with date codes of 1208
  • MNL-V2 starting with date codes of 1212

Note: The MNL VAV control range of 0.05 to 2.00 in. WC (12.5 to 498.2 Pa) is not affected. When air flow control below 0.05 in. WC is required, the I/A Series MNB VAV controllers, with a control range of 0.004 to 1.5 in. WC (1.0 to 373.6 Pa), should be used.

MNL Firmware Updater Utility

The MNL Firmware Updater 4_3B5.zip can be downloaded from The Exchange Download Center. The zip file contains these instructions and the “MNL Updater Setup.exe”. Executing “MNL Updater Setup.exe” will place the latest firmware into C:\Program Files\Schneider Electric\MNL Firmware Updater\bin and add the installer to the Start Menu item under Schneider Electric.

  • MNL-V1RV3-2, MNL-V2RV3-2, and MNL-V3RV3 controller firmware version 4.3B5
  • MNL-5 controller firmware version 4.3A5

If the MNL Firmware Updater had previously been installed, the MNL-V1RV3.NDL, MNL-V2RV3.NDL, and MNL-V3RV3.NDL files located in "C:\Program Files\Schneider Electric\MNL Firmware Updater\bin" will be replaced.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 12240
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now