Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

I/A Series G3 I/O modules (TRD-T-IO-16 or TRD-T-IO-34) cannot be discovered and do not communicate "right out of the box."

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A Series G3 I/O modules (TRD-T-IO-16 or TRD-T-IO-34) cannot be discovered and do not communicate "right out of the box."
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1426 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A Series G3 I/O modules (TRD-T-IO-16 or TRD-T-IO-34) cannot be discovered and do not communicate "right out of the box."

Picard Product_Support
‎2018-09-10 12:40 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:46 AM

Issue

Customers are reporting that TRD-T-IO-16 and TRD-T-IO-34 modules do not communicate "right out of the box". The "PWR OK" led on the IO-34 is lit up, but the device remains undiscoverable in Workbench (in the Ndio Board Manager view). The IO-16 has no LEDs lit, and also cannot be discovered. The IO modules are brand new, unused units.

Environment

I/A Series G3, TRD-T-IO-16, TRD-T-IO-34

Cause

The IO-16 or IO-34 module was initially powered up for too brief a time and then powered off, interrupting an "automatic IO firmware upgrade" that was underway. The JACE keeps the latest NDIO firmware in its image distribution, and automatically updates any attached IO module found with older IO firmware. This IO firmware upgrade process occurs for each attached IO module, in sequence, starting with the lowest logical address IO board (IO module closest to JACE). During an IO firmware download, the JACE's Status LED has a long duty cycle blink -- long On, blinking Off.

This IO firmware upgrade takes at least 30 seconds for each IO-16 module, and at least 60 seconds for an IO-34 module. Therefore, if multiple IO modules are attached with older IO firmware, it can take as long as 4 minutes of uninterrupted power to safely complete this operation. Once completed, the JACE continues booting and starts its platform daemon process. Therefore it is always safe to cycle power to the JACE once a platform connection can be made.

Resolution

If the JACE is powered down or if the IO module is removed during this IO firmware update, the IO module becomes unusable and must be returned to the factory to be re-imaged. The "PWR OK" LED will show green on an IO-34 even after is has been broken this way, but it will remain undiscoverable and unusable.

Reference TPA-IA-12-0004-00 for more details.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 10984
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore