Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

I/A Series G3 ENC time of day clock runs slow

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A Series G3 ENC time of day clock runs slow
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1348 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A Series G3 ENC time of day clock runs slow

Picard Product_Support
‎2018-09-10 05:50 AM

Issue

I/A Series G3 ENC time of day clock runs slow.  Can this be corrected in the field?

Product Line

TAC IA Series

Environment

I/A Series G3 ENC (remanufactured replacement)

Cause

The time clock constant was incorrectly set in some remanufactured ENC-520 controller boards. The result is that the ENC-520 time clock (time of day clock) will not maintain proper time.

Resolution

  1. jumper.pngConnect to the ENC using the Serial adapter and a Windows Terminal program such as HyperTerminal. If you need information on how to use the Serial Shell (terminal connection), refer to Chapter 1 (Recover Tips, Serial shell, page 26) of the "Jace Niagara -AX Install and Startup Guide," found in the Docs folder of your 3.5.34 installation directory.
  2. Make sure that you have installed a jumper on the outer pair of pins of the MODE connector (upper right corner of circuit board -- see photo at right).
  3. Reboot the ENC by disconnecting and reconnecting the power plug.
  4. Allow the ENC to reboot and wait for the login prompt to be displayed in your terminal program.
  5. Log in using the hardware user name and password.
  6. Wait for shell menu and the "Enter Choice" prompt to be displayed.
  7. Type sh and press enter.
  8. At the # prompt, type lfss -c and press enter.
  9. The current clock multiplier will be displayed. I expect that the current multiplier is 96000000.
  10. Type lfss -c 96065600 and press enter. Wait for the # prompt to be redisplayed.
  11. Verify that the entry was properly entered by typing lfss -c and pressing enter .
  12. The value 96065600 should be displayed.
  13. Type exit and press enter to return to shell menu.
  14. Press 7 to reboot the ENC. Press y to confirm the reboot and press enter.
  15. The ENC will reboot. Remove the mode jumper and disconnect the serial cable.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 6995
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of