I/A Series G3 ENC-SW (Soft JACE) warning - Database resources exceed licensed capacity. Station may not restart.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A Series G3 ENC-SW (Soft JACE) warning - Database resources exceed licensed capacity. Station may not restart.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1634 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A Series G3 ENC-SW (Soft JACE) warning - Database resources exceed licensed capacity. Station may not restart.

Picard Product_Support
‎2018-09-06 03:51 PM

Issue

I/A Series G3 ENC-SW (Soft JACE) warning - Database resources exceed licensed capacity. Station may not restart.

Environment

I/A Series G3 ENC-SW (all versions)

Cause

The I/A Series G3 ENC-SW (Soft JACE) operates with a capacity limit based on Java Resource Units (kRU).  The base ENC-SW-1M includes 10 Million resource units (10,000 kRU).  ENC-SW-2MU can be added to increase the resource units by 20 Million for a total of 30 Million resource units (30,000 kRU).

Upon station start, the software will analyze the database and calculate the current resource requirements.  This includes resources used for steady state runtime as well as resource allocation required to archive records (histories, trends, alarms, etc.). The software compares the calculated resource value against the license and generates a warning if the total exceeds the licensed limit.  The warning states "Database resources exceed licensed capacity. Station may not restart. Contact your vendor to acquire additional capacity."

When a resource limit is specified in the license, exceeding the limit will result in the station failing. The entry in the I/A Series G3 ENC-SW license unique to a Soft JACE is the “resource.limit” number found in the “station” section.

        expiration="never"
        resource.limit="10000"
        parts="SJ-1M-AX"/>

In this license example, any station running on the Soft JACE is limited to a maximum of 10 Million resource units (10,000 kRU).  A station operating above this will generate a yellow highlighted warning in all views of the station, including wire sheets, property sheets, and Px views even when accessed via the browser.

ENC-SW resource limit exceeded warning (seen in any view of its station)

Resource limit exceeded warning

Furthermore, as the warning informs, the ENC-SW station may not restart. ENC-SW station restart failure example.

Station failure message

You can check the current resource unit count of any running station currently opened in Workbench. To do this, right-click the station node in the Nav tree, and select Views > Resource Manager. 

Resource Manager reports resource limit and current total

Resource Manager

Resolution

If the existing ENC-SW is licensed for 10 Million resource units (10,000 kRU), purchase additional resource units (ENC-SW-2MU) to increase the total to 30 Million resource units (30,000 kRU).  Otherwise, review the "steady state" resource count and decrease the Capacity (Record Count) of trends and alarms to reclaim resources used for record allocation and maintain a safety buffer below the resource limit.  Note: History information may be lost is the limit is exceeded.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 7860
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore