How to use the pull-up resistor of Continuum I2/B3 controllers' input?
  • How to use the pull-up resistor of Continuum I2/B3 controllers' input?
  • Zhenting_HU
    Zhenting_HU
‎2018-09-10 11:06 PM
If the pull-up resistor is disabled falsely, the sensor value or status that connects with this input may be wrong. For example, sensing temperature value has a great deal of error with the actual temperature value.
I2 controllers
B3 controllers
If the pull-up resistor selection is wrong, the right value can not be gotten.
The following is a schematic representation of the switch and its associated pull-up:
 pull-up
  1. To measure temperature, the pull-up resistor switch associated with this input must be enabled.
  2. To measure voltage, the pull-up resistor switch associated with this input is usually disabled (OFF).
  3. To sense contact closures (Digital signals), the pull-up resistor switch associated with this input must be enabled.
  4. To count Pulsing signals or contact closures, the pull-up resistor switch associated with this input must be enabled.