Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to use the Piecewise command in Sigma Graphics.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to use the Piecewise command in Sigma Graphics.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • RogerHa
    RogerHa
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1521 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to use the Piecewise command in Sigma Graphics.

Product_Support
‎2018-09-06 12:36 PM

Last Updated: CraigEl Champion ‎2025-10-12 08:52 PM

Issue

When displaying a multi-value status from a programmable object in Sigma Graphics, updates may not reflect correctly unless the object value changes significantly (e.g., from 0 to 100). This can cause display issues when the graphic is open and the state changes.

Product Line

Satchwell BAS & Sigma

Environment

Sigma Graphics Ver 4.0 onwards

Cause

Sigma Graphics does not automatically update the display unless the programmable object’s value changes in a way that triggers a refresh. This is problematic when using objects that return multiple discrete states.

Resolution

Use the Piecewise command with stacked text objects to display the correct state visually.

Step-by-Step Workaround

  1. Create a Programmable Object
    Example logic:

    10 IF POINT 0|123 = 1.00000 THEN RETURN TRUE "Off"
    20 IF POINT 0|123 = 2.00000 THEN RETURN TRUE "Text No1"
    30 IF POINT 0|123 = 3.00000 THEN RETURN TRUE "Text No2"
    40 IF POINT 0|123 < 1.0 OR POINT 0|123 > 3.0 THEN RETURN "Invalid"
    
  2. Design the Graphic

    • Create three text objects:
      • 1 – Off
      • 2 – Text No1
      • 3 – Text No2
    • Stack them vertically with "Off" at the bottom.
    • Align them precisely over each other to form a single visual stack.
  3. Combine and Configure

    • Select all three text objects and combine them into one.
    • Assign a Piecewise command to the combined object:
      • Object: 123
      • Min: 1
      • Max: 3
  4. Behavior

    • The graphic will display the appropriate text based on the object’s value.
    • If the value is 0 or greater than 3, the display will be blank.

Notes

  • This method works best with analog values from programmable objects.
  • Variations are possible depending on the number of states and desired display behavior.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (3)
  • Find more articles tagged with:
  • 7452
  • CraigEllis25
  • minimum
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore