When you log in to the Xenta via a webinterface and choose utilities you can choose to view some reports.  The time stamp on different reports are used differently.
When you log in to the Xenta via a webinterface and choose utilities you can choose to view some reports "Error" and "System report"
When you open up the Error report you can see this information on top of the screen (System Error Log - Compiled "Date") The Date field are set to the Date and Time you pressed the link, This is because the report are generated the minute you press the link.
When you open up the System Report you can see this information on top of the screen (System information overview "Date") The Date field are set to the Date and Time the last event came in (approximately).
You also have the System Information log. When you click on this you will see on top System information overview "date" Where the date will be set to the minute you press the button. This is because the report are generated when you click the link.