How to transfer values between Menta object within the same Xbuilder project.
  • How to transfer values between Menta object within the same Xbuilder project.
  • sesa150555
    sesa150555
‎2018-09-06 12:28 PM
TAC Xbuilder
Sometimes there is a need to transfer values between Menta applications in the same Xbuilder. To do this you create an input in the receiving node.
  1. In Xbuilder open the Menta application that you want to read a signal from another Menta application
  2. Add a input block of the type the signal will be (II, RI or BI) save to  Xbuilder.
  3. Right click on the input in the system pane and select "select signal"
  4. Browse to the signal you want to transfer.