How to transfer a XBuilder project to a different type of Xenta Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to transfer a XBuilder project to a different type of Xenta Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa139513
    sesa139513
  • DavidFisher
    DavidFisher
  • LeeCravens
    LeeCravens
  • Benji
    Benji
  • sesa115370
    sesa115370
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2165 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to transfer a XBuilder project to a different type of Xenta Server

Picard Product_Support
‎2018-09-06 10:35 AM

Issue

Prior to XBuilder 5.1.1, it was not possible to change the type of an Xenta Server in an XBuilder project once it had been created.  Sometimes there is a need to move the project to a different type of Xenta Server without losing all the links and bindings within the project.

Environment

Xenta Server

XBuilder 5.1.0 or earlier

Xenta 511, 527, 555, 701, 711, 721, 731, 913

Cause

In XBuilder 5.1.0 or earlier, it is not possible to edit the Xenta Server type in the network pane of the XBuilder project

Resolution

Upgrading to Vista/XBuilder 5.1.1 or later will allow you to easily change the device type directly from XBuilder.  Note that this must be done from an XBuilder project that is saved to the computer. If the project is in a Vista database start by opening the XBuilder project, clicking on File > Save as and then save it to the computer. Then, close XBuilder, reopen XBuilder and open up the saved copy of the XBuilder project from the PC. In the XBuilder Project menu select 'Change Target type...'.  Choose your preferred target device from the drop-down list.
 
If it is not possible to upgrade, the following instructions allow an XBuilder project to be transferred to a different type of Xenta Server without losing graphic bindings or bindings between objects on the System pane and the Network pane.  The one proviso is that the target Xenta Server's hardware must be able to support any network defined in the source project and have the same or better Menta and User graphic capabilities.
 
There are many different combinations of Server types and BMS platforms that these instructions could apply to in general.
 
The example given here transfers an Xenta 555 project to an Xenta 731.  The Xenta 555 has a Lonworks network and a Modbus network and is part of a Vista database.
 
Creating the Xenta 731 in the Vista database:
  1. Open the Vista database containing the Xenta 555 project.
  2. Right-click on the 555 and select Edit from the dropdown menu.
  3. The XBuilder project opens.  Keep this open for the following steps.
  4. In the Vista database create a new Xenta 731.  The name is not important but it should be similar but not identical to the 555 it will replace.

Transferring the Lonworks network to the Xenta 731:

  1. In Vista, drag and drop the LON network from the 555 to the 731.
  2. Right-click on the 731 and select Edit from the dropdown menu.
  3. The 731 project opens in a new instance of XBuilder.  Rename the default folder in the system pane to the same name as the top level folder in the 555 project.
  4. In the 731 project right-click on the LON object in the Network pane.  Select 'Refresh network from TAC Vista'.

Transferring the Modbus network to the Xenta 731:

  1. In the 555 project, right-click a Modbus device and select 'Edit Device template'
  2. When the device editor opens, select File | Save as..
  3. Save the file in the default location with the default name.
  4. Repeat steps 2 to 3 for all Modbus devices in the network.
  5. In the 731 project recreate the Modbus network using the templates just saved.

    Transferring the System objects to the Xenta 731:

  1. In the 555 project, right-click an object below the top level folder and select 'Copy'.
  2. Move focus to the 731 project, right-click on the top level folder and select 'Paste'.
  3. Repeat steps 1 and 2 for each object and folder below the top level in the 555 project.  Selecting a folder also selects all the objects and folders beneath it.  Although it is possible to copy the top level folder in the 555 project, it is not possible to paste it into the 731 project.
  4. Graphics bindings are retained and the reference paths are automatically updated with the new network tree i.e. 'TAC_Xenta_555' is replaced with 'TAC_Xenta_731'.
  5. Some object bindings will be broken e.g. Time objects.  These must be rebound manually.
  6. When all objects have been copied across and rebound if necessary, close the 555 project.

Deleting the Xenta 555 and downloading the project to the Xenta 731:

  1. In the Vista database, delete the Xenta 555.
  2. Generate the 731 project.  There will be a warning message offering to copy the original TGML files to the new default location.  Select 'Yes'.
  3. The 731 project should now generate without errors.
  4. Download the project to the Xenta 731.

 

If the 555 only contains a Modbus network, a similar methodology will also work with standalone 555 and 731 projects.
 

Labels (4)
Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 12734
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore