How to tell ACC Infinity37 cards from other card formats with same 37 bit count

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to tell ACC Infinity37 cards from other card formats with same 37 bit count
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • AbeMeran
    AbeMeran
  • Omaelk
    Omaelk

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2649 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to tell ACC Infinity37 cards from other card formats with same 37 bit count

Captain AbeMeran Captain
‎2022-04-04 01:25 PM

Last Updated: Janeway Omaelk ‎2022-10-19 12:58 AM

Issue

37-bit cards not working correctly even though a Credential Type has been configured correctly for Infinity37 cards (as seen below), the site code and/or card number read does not match what is printed on the card or the expected value.

Parity errors could also be seen if the card is not truly of the Infinity37 format.

2022-04-04_14-54-49.jpg

Product Line

Security Expert

Environment

  • Security Expert Server
  • Security Expert Controller

Cause

Various cards have 37-bit data lengths but different formats; some guidance is needed on how to differentiate the ACC Infinity37 cards. 

Resolution

There are two pieces of data that can be used to verify if a 37-bit card is ACC Infinity27 format.

 

  1. ACC Infinity 37 card format includes a Manufacturer's Code field; the field is 4 bits long, starting on the second bit and ending on the fifth bit. The Manufacturer's Code field always has a value of 4, the first bit of the card is used for the ODD parity, so the first 5 bits of ALL ACC Infinity37 cards ALWAYS look like P0100....Inf37Cards.jpg
  2. If we see a raw bitstream of a 37-bit card like the one in the screen capture below, we can immediately determine that even though the card has 37 bits, it is NOT an Infinity37 card since bits 2,3,4 and 5 do not add up to a value of 4
    NonInf37Card.jpgNonInf37Card2.jpgSee https://community.se.com/t5/Building-Automation-Knowledge/How-to-display-RAW-bit-data-stream-of-Wieg... 
  3. We can not assume that because a 37-bit card has  0100 on bits 2-5 it is 100% evidence that the card is indeed an Infinity37 card since that pattern (0100) could be present on the card as part of a different field (i.e., Site Code) on a different 37-bit card format. The second piece of data that could help determine if the card is true of the Infinity37 format is the parity bits, Infinity37 card format has a somewhat unique interlaced parity scheme. If parity errors are seen when cards are presented to the reader, this should be taken as an indication that the 37-bit card might not be Infinity37 card format.
  4. The attached zip file contains an Excel sheet that can be used to calculate the parity bits of an ACC Infinity37 card by entering the raw bitstream of the card; if the calculated values for both parity bits (bits 1 and 37) do not match what the card has, then the card is NOT an Infinity37 card format.

 

 

Labels (1)
Labels:
  • EcoStruxure Security Expert
Attachments
ACCInf37ParityCalculator.zip
Tags (7)
  • Find more articles tagged with:
  • 37
  • AbeMeran22
  • bits
  • card
  • format
  • infinity37
  • parity
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore