How to sound a buzzer when a Request To Exit (REX) button is pressed?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to sound a buzzer when a Request To Exit (REX) button is pressed?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PaulFr
    PaulFr
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2427 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to sound a buzzer when a Request To Exit (REX) button is pressed?

Picard Product_Support
‎2018-09-06 02:10 PM

Issue

How to sound a buzzer when a Request To Exit (REX) button is pressed on a Continuum Access system? The inputs to a door are not defined as regular Infinity inputs so how can they be programmed by Plain English programming?

Environment

ACX57xx (ACX5740, ACX5720) and AC-1 IOU modules (AC-1, AC-1A, AC-1 Plus)

Cause

When engineering an access control project, there is sometimes the requirement to sound a buzzer or turn on a light when the door is unlocked, or when a Request To Exit button is pressed, as the input points used within the door object configuration are not defined as a regular Infinity Inputs, so how to achieve this functionality?

Resolution

To use a Request To Exit (REX) switch on any of the ACX controllers or AC1 Modules:

  1.  It has to be a supervised input wired with the appropriate resistors in one of the 6 standard configurations defined in the installation guides (All available on the Extranet).
  2. You can not use a simple digital input switch without resistors.
  3. Incorrect circuitry or missing resistors will result in a Trouble indication on the door.
  4. The REX input is not a regular Continuum input point as it is defined within the door configuration, as it is not a Infinity input point directly accessible from Plain English but can be read via the "ExitRequest" attribute of the door.

To sound a buzzer from the from the door there are 3 options:

  1. Use the existing door output and slave a buzzer circuit from the output that drives the Magnetic lock, so will sound when the door unlocks.
  2. If you want the buzzer to sound when the REX button is pressed then use a button with a 2 pole switch (2 separate contacts):
    1. Wire one to the REX input with appropriate resistors.
    2. Wire the other switch to a spare Input
    3. Configure it as either a Digital input or a Supervised input with resistors.
    4. This point can be used in your PE programming to drive the buzzer output.
  3. The third option is to use a Plain English program to read the "ExitRequest" attribute of the door and turn on an output for a defined time. The ExitRequest attribute may only be on for a short period of time so the program must be constantly looking for this attribute to change as well as keeping the controller Scan time low.

 

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 4549
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore