How to show person name in invalid attempt alarm of a door.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to show person name in invalid attempt alarm of a door.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1289 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to show person name in invalid attempt alarm of a door.

Picard Product_Support
‎2018-09-06 01:57 PM

Issue

Need to show the name of a person triggering invalid attempt alarm at a door in the alarm's feedback message.

Environment

CyberStation

CX9702

CX9900

CX9680

ACX5720

ACX5740

ACX701

ACX781

Cause

Alarm engine does not provide functionality natively to display personnel name on invalid attempt at a door, Plain English program must be used.

Resolution

The basic idea is to set the door’s description to the value of the door’s LastInvalidEntry (or LastInvalidExit) attribute, and use the wild cards %N and %D to embed the Door’s name and LastInvalidEntry (or LastInvalidExit) into the alarm’s feedback messages.

Since the controller is unable to resolve the path to the personnel object pointed to by lastInvalidEntry/LastInvalidExit a CyberStation program is needed.

Also, because the InvalidAttempt flag of the door only persists for one scan it is necessary to latch its value into a numeric point.

In the controller write a looping program to latch the value of the door’s InvalidAttempt flag.

CONTROLLER PROGRAM

1:

  If Vault_Door InvalidAttempt then

    VaultDoorInvalid = 1         <---VaultDoorInvalid is a numeric point in the controller

    Goto 2

  Endif

 2:

  If VaultDoorInvalid = 0 then Goto 1

CYBERSTATION PROGRAM

 Write a program in CyberStation to monitor VaultDoorInvalid and set the door’s description to LastInvalidEntry

  WaitForInvalid:

  If LocalNetwork\ACX2.13\VaultDoorInvalid then

    Print LocalNetwork\ACX2.13\Vault_Door LastInvalidEntry to STR1

    Goto SetDrDescription

  Endif

 SetDrDescription:

  LocalNetwork\ACX2.13\Vault_Door Description = STR1  <--- STR1 is a String object in CyberStation

  Goto ResetFlag

 ResetFlag:

    LocalNetwork\ACX2.13\VaultDoorInvalid = 0

   If LocalNetwork\ACX2.13\VaultDoorInvalid = 0 then Goto WaitForInvalid

 ALARM ENROLLMENT

 Lastly, create an expression AlarmEnrollment , set it to

            Description <> “”

And attach it to the door.

 When an invalid attempt is detected the alarm stays ON until the door object is edited (from the alarm view itself) and the description cleared.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 4931
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore