Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Launch of Consumer/Home Owner registration process!
We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.

How to setup a local time chart to have an alternative time schedule for holidays?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to setup a local time chart to have an alternative time schedule for holidays?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Anonymous user
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1568 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to setup a local time chart to have an alternative time schedule for holidays?

Picard Product_Support
‎2018-09-10 03:16 AM

Issue

On a special holiday, sometimes it is necessary to specify an alternative time schedule to overwrite the original time schedule. For example, an AHU normally turns on from 8:00AM to 5:00PM, however, on the New Years day, this AHU needs to be turned on only from 13:00 PM to 15:00 PM.

Unlike the Xenta time schedule which is created in Menta, Vista server local time schedule does not have the option to point to an alternative time schedule. Therefore, how to setup the local time schedule in TAC Vista Workstation in order to achieve this result?

Environment

  • TAC Vista Workstation
  • TAC Vista local time schedule
  • Tested on Vista 5.1.6

Cause

Since Vista server local time schedule (also called Time Chart-Local) does not have the option to point to an alternative time schedule like Xenta time schedule does, users need to specify the alternative schedule within the local time schedule by specific steps which are described in the resolution.

Resolution

Since Vista server local time schedule’s alternative time schedule options’ priorities are according to the order when they were created (newer alternative chart has higher priority). It is necessary to create a “OFF all day” alternative chart to overwrite the regular schedule before create the actual time schedule for the special occasion date.

  1. Open the local time schedule by double click on it or right click and choose “Properties”.

     
  2. Click on “New…” in “Event” section. Then,
    1. Uncheck “Weekly” and specify the special occasion date.
    2. Select “OFF all day” under “Time” section.
    3. Choose “Select all” under “Valid weekdays”.
    4. Click “OK”.
       
  3. Repeat step 2 to create another schedule to cover the actual holiday schedule. Choose “Specify time” instead of “OFF all day” under “Time section” in this step.

The alternative time schedule should work by now.



 

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 6315
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore