Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

How to set up a MicroNet Mi for use on a Xenta 555

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to set up a MicroNet Mi for use on a Xenta 555
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • Gary
    Gary
  • DavidFisher
    DavidFisher
  • sesa119747
    sesa119747
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2124 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to set up a MicroNet Mi for use on a Xenta 555

Picard Product_Support
‎2018-09-06 02:28 PM

Last Updated: Sisko DavidChild Sisko ‎2019-06-21 02:57 AM

Issue

How to set up a MicroNet Mi for use on a Xenta 555

Product Line

Satchwell MicroNet

Environment

  • MicroNet Mi
  • Xenta 555

Cause

Installation instruction for setting up MicroNet Mi with Xenta 555.

Resolution

Updated June 2019

The MicroNet 50 series range MN350, 450, 550, 650 LCD and Touchscreen have been withdrawn from sale.
The IAC 420, 600 and Touchscreen have now also been withdrawn from sale.
No direct replacement is offered.
Further information on these changes can be found in PA-00495 - Notice of Withdrawal - Satchwell Sigma and PA-00528 - End of Commercialization - Satchwell Sigma.

----------------------------------------------------------------------------------------------------------------------------------------------------------

  • Cold start the MN50-Mi-ARC or MN-MI-100 with ARCnet card (MN-Mi).
  • Unplug any RS 232 cables that are connected to PL3 or PL4.
  • Energise the MN-MI and verify that the RUN LED flashes at about once per second.
  • Set all bit switches to off.
  • Place bit switch 8 to the on position and then return to OFF position.
8 On.jpg
  • Place bit switch 1 to the ON position.
1 On.jpg
  • Place bit switch 8 in ON position and then return to OFF position.
1 and 8 On.jpg
  • The RUN, WINK and MODEM LEDs remain lit for about 1.5 seconds, and then the RUN LED should flash at about once per second.
    Note: This is different from the cold-start procedure for a controller, which requires you simply to toggle switch 8.
  • Plug the RS 232 cables to PL3 or PL4.
  • Connect the Xenta 555.
Labels (1)
Labels:
  • Satchwell MicroNet
Attachments
Tags (2)
  • Find more articles tagged with:
  • 3880
  • GaryMontague19
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of