How to set attributes on all objects of a given class in a controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to set attributes on all objects of a given class in a controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1076 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to set attributes on all objects of a given class in a controller

Picard Product_Support
‎2018-09-06 12:55 PM

Issue

Sample PE program for setting attributes on all objects of a given class in a controller.

Environment

ALL CX Controllers.

Cause

The following PE program is a sample of a program that sets the site codes on ALL the doors found in the controller upon the controller power up.

Resolution

'This program sets the site codes on all the doors in this controller
'Program is autostart and fallthru
'Program is triggered by the MINUTE system variable
'12/16/2011 Abe Meran
'Sample program

Datetime LastStartUp
Object theDoor

INIT:
  LastStartUp = PowerUpTime
  Goto WAIT1

WAIT1:
  If PowerUpTime > LastStartUp then Goto RESET_SITE_CODE

RESET_SITE_CODE:
  OpenList("Door", theDoor)
  While GetObject(theDoor) is Success
    If theDoor Site1 = 0 then theDoor Site1 = 1
    If theDoor Site2 = 0 then theDoor Site2 = 2
    If theDoor Site3 = 0 then theDoor Site3 = 3
    If theDoor Site4 = 0 then theDoor Site4 = 4
  Endwhile
  CloseList(theDoor)
  Goto WAIT1

E:
  CloseList(theDoor)
  Goto WAIT1


Here is another example of a program residing in a CX that sets the site codes on all the doors of all the ACXs under the CX

Object theACX
Object theDoor
Number OK

If OpenList("InfinetCtlr", theACX) is Success then
  While GetObject(theACX) is Success
    If OpenList("Door", theDoor, theACX) is Success then
      While GetObject(theDoor) is Success
        theDoor Site1 = 1111
        theDoor Site2 = 2222
        theDoor Site3 = 3333
        theDoor Site4 = 4444
      Endwhile
    CloseList(theDoor)
    Endif
  Endwhile
Endif
Goto 2

2:
  CloseList(theACX)
  CloseList(theDoor)
Stop

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 6875
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore