How to select a platinum sensor compatible with the Analog Input (AI) object in WorkPlace Tech.
  • How to select a platinum sensor compatible with the Analog Input (AI) object in WorkPlace Tech.
‎2018-09-06 02:07 PM
on ‎2018-09-06 02:07 PM
WorkPlace Tech
I/A Series Lon (MNL) controllers
I/A Series BACnet (MNB) controllers
Sensor manufacturers provide platinum sensors with different Temperature Coefficient of Resistance (TCR).
The Analog Input (AI) object supports 1Kohm platinum sensor with Temperature Coefficient of Resistance (TCR) equal to 0.00385 OHM/OHM @ °C.
Check manufacturer's datasheet and select sensor with TCR of  0.00385 OHM/OHM @ °C
  • TAC IA Series
  • 4642