How to read the Setpoint potentiometer of a TSMN-90250-850 room sensor in an MNL-800.
  • How to read the Setpoint potentiometer of a TSMN-90250-850 room sensor in an MNL-800.
  • SESA113595
    SESA113595
‎2018-09-06 10:49 AM
MNL-800
Need to scale the voltage inputs in the AI object in the MNL-800 application.
Connect:
SP+ to the 5.1VDC source on the MNL-800
SETPT to the INx input on the MNL-800
COMMON to C on the MNL-800.
Might need to adjust the UI configuration in the MNL-800,  here's starting point:
Add the SP to a UI on the MNL-800.  In the AI object  with Low Value = 0, Scaled Low value = 94.7 deg; High Value = 5 , Scaled High = 47.1 deg F.
  • TAC IA Series
  • 12019