Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

How to prevent the Niagara R2 UNC station from sending multiple messages when emailing an alarm to a Cell Phone.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to prevent the Niagara R2 UNC station from sending multiple messages when emailing an alarm to a Cell Phone.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1400 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to prevent the Niagara R2 UNC station from sending multiple messages when emailing an alarm to a Cell Phone.

Picard Product_Support
‎2018-09-06 02:38 PM

Issue

How to prevent the Niagara R2 UNC station from sending multiple messages when emailing an alarm to a Cell Phone.

Environment

I/A Series R2 station

Cause

If a message sent to a cell phone as a text message exceeds a specific number of characters, the receiving phone will usually split the message into more than one part.  These message segments may not always be delivered in sequential order.

Resolution

Limit the number of fields defined to be transmitted in the alarm message. This field information is configured in the properties of the MailRecipient object. Remember that each selected field will appear in the message on a separate line.
An alarm message sent as an e-mail message includes the Subject property, address properties (To, From & CC) and selected formatted alarm data fields. The message is formatted by the cell phone service provider based on their message delivery protocol.

The exact e-mail delivery technique varies from one cell phone service provider to another.

For example, the service providers US Cellular, ATT/Cingular or Sprint, deliver e-mail messages as a series of SMS (Short Message System) messages. The limit for each SMS message is 160 single-byte characters. To format the message into SMS format, the carrier breaks the message into 160 byte chunks and delivers these chunks as a series separate messages to the recipient's cell phone.

Some cell phone service providers use MMS messaging (Multimedia Message Service) to transmit e-mail messages to users subscribed to this feature.  With MMS, the e-mail message is typically received as a single message, however, only the message header (To, From and Subject) will be delivered to the phone until the user attempts to read the message. When the user opens a message in this format, the cell phone uses WAP (Wireless Application Protocol) to retrieve the message from the service provider and display the entire message. Note that to read the entire message, the user must have access to his carrier's network at the time he is attempting to read the message.

UPDATE:
US Cellular has announced that in selected service areas, they will offer a new service on specific phones that will allow sending and receiving HTML (text) based e-mail messages without the 160 character limitation.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 3431
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of