Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

How to override a block output (DO or AO) in a MicroZone II controller on the ASD bus under a G3 ENC.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to override a block output (DO or AO) in a MicroZone II controller on the ASD bus under a G3 ENC.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • SESA113595
    SESA113595

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1344 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to override a block output (DO or AO) in a MicroZone II controller on the ASD bus under a G3 ENC.

Picard Product_Support
‎2018-09-10 10:30 PM

Issue

How to override a block output (DO or AO) in a MicroZone II controller on the ASD bus under a G3 ENC.

Environment

I/A Series ENC-520 with an ASD bus under it.

Network 8000  ASD controller (LIM1, MicroFlow II, MicroZone II, PEM1)

Cause

Need to document the process for discovering controllers, the blocks they contain, and  adding the block attributes to the G3 station so that the desired points can be over-ridden.

Resolution

The complete process of discovering a MicroZone, the blocks it contains, and adding the block attribute to the database is illustrated in the following series of screen captures.

While the DV of a DO block in a MicroZone II application is shown, the same procedure will work with other blocks in the other ASD controllers.

NOTE*     Step 11 is not documented , and is commonly over-looked.

1. The MicroZone II is connected to the ASD bus, but it has not been added to the AsdNetwork in the station yet.

 

2. Right-click on the AsdNetwork, select Asd Device Manager from the menu.

 

3. In the Asd Device Manager, the 2 devices that have already been discovered are shown in the upper pane. To discover the MZ2, click on the Discover button at the bottom of the pane.

 

4. This brings up the Discovery Filter, where the type(s) of controller(s) and their address range(s) can be selected for discovery. In this case, only MZ2s will be searched for, in the default address range of 1 -32.

5. The Microzone II with address = 1 has been discovered by the Asd Device Manager, and "Success" is indicated in the status bar. The device has not been added to the database yet.

6. To add the MZ2 device to the database, click on the Mz2 device in the upper "discovered" pane, then click on the "+ Add" button at the bottom of the Database pane.

7. Pressing the "+ Add" button brings up the Add window, where the attributes of the device are displayed and can be edited.  In this case, the default values are all used.

8. A device object for the mz2_1 has been added to the AsdNetwork and is displayed in the tree on the left side pane. Expand the mz2_1 object, right-click on the "Points", and  select the Asd Block Manager from the Views menu.

9. In the Asd Block Manager, no blocks are shown yet for the mz2_1 device. Click on the Discover button at the bottom of the Database pane to discover the blocks in the MicroZone II controller.

10. When the blocks have been learned, "Success" is displayed in the Asd Learned Blocks status bar, and 25 objects have been discovered.  Expand DO 1 to expose the DV block attribute under it. This is the controller output that will eventually be over-ridden.

11. Click on the DV to highlight it, then press the "+Add" at the bottom of the database pane to add the DO 1 block's DV attribute to the station database. This will bring up the Add screen as shown below. Click OK to add the object.

12. Now the DO1 block and it's DV output have been added to the station database as a Boolean point. In the tree on the left expand the Points folder under the mz2_1 object. Right-click on the DO1_DV point, and select "override" from the Actions menu.

13. The override window is displayed, where the Time and Value of the override can be set. In this case, DO1_DV will be overridden ON (true) for 10 minutes when the OK button is pressed.

Note: Entering a time of 0 minutes will result in a permanent override.

14. The block output has been overridden, and is displayed in the Database pane of the Asd Block Manager view.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 10994
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of