How to order a controller with or upgrade a controller to have XDriver support

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to order a controller with or upgrade a controller to have XDriver support
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3211 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to order a controller with or upgrade a controller to have XDriver support

Picard Product_Support
‎2018-09-07 06:00 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:45 AM

Issue

How to order controllers with XDriver support
How to upgrade a controller so it has XDriver support
All NC2 options are not available as standard
How to order node upgrade

XDriver X-Driver X Driver

Product Line

Andover Continuum

Environment

2nd Generation Controllers with X Driver Port enabled

NC2, NCII, Netcontroller 2 CX9680
bCX1, bCX9640 bCX4040  not bCX4000
ACX57xx ACX5720 ACX5740
CX9702 - No XDriver Support
X-Drivers 

Cause

If the NC2 controller required has non standard XDriver requirement, then a standard unit must be ordered, then later upgraded

Resolution

  1. NC2 (NCII, NetController 2, CX9680)
    This unit is only available with XDriver enabled on Comm1 (as an option). If other comms ports are required to have XDriver support then this can be ordered after the NC2 is received by ordering the upgrade (you need the serial number before the upgrade order can be processed) via your normal order entry facility.
    Option tab - example NC2
    Xdriver Comm1 : 00000009 (0000)  (XDriver enable and but not loaded)
    Xdriver Comm2 : 00000000 (0000)  (XDriver not enabled)
    Xdriver Comm3 : 00000000 (0000)  (XDriver not enabled)
    Xdriver Comm4 : 00000000 (0000)  (XDriver not enabled)
    Only the NC2-F (fitted with FTT10 Lon IO option) can support the Echelon XDriver, this is enabled via the Web interface and loaded on to Comm16 in the usual way. If this Comm Port is used for an XDriver, then no IO can be connected to the NC. (This is a no cost option and does not require an upgrade)
  2. bCX bCX9640 bCX4040 - NOT bCX4000
    The bCX has two comms ports, the XDriver functions can be enabled on none, either or both at the time of ordering (add X1, X2 or X12)
    Option tab - example bCX
    Xdrvr Comm1:00000009 (DF23)  (XDriver enable and loaded)
    Xdrvr Comm2:00000000 (0000)  (XDriver not enabled)
  3. ACX ACX5720 ACX5740
    The ACX57x0 has a single comm port, the XDriver functions can be enabled at the time of ordering (see the
    Option tab - example ACX57
    Xdriver Comm1 : 00000009 (0000)  (XDriver enable and but not loaded)

NOTES

  • 00000000=XDriver not enabled, 00000001=CommPort only, 00000009=CommPort & Ethernet enable, 00000011=CommPort & Access API enable (Schlage, Assa Abloy etc)
  • The four digit number in bracket shows which Xdriver is load and corresponds to "Xdriver valid" at the bottom of the xdriver.xdr file.
  • If Ethernet support is required on the port then this should be requested at the time of ordering.
  • XDrivers like Modbus TCP/IP and Bacnet IP are loaded on to a comms port but communicate via the Ethernet port, therefore the XDriver Ethernet support needs to be enabled for these XDrivers to operate.
  • The XDrivers and hardware update forms are available for download: For orders submitted through Sweden | For orders submitted through the U.S.
  • If an Xdriver requires removing, then go offline, select the comm port, change to Autoset, return online then reload the controller
  • Other upgraded to controllers, eg. node count upgrade is dealt with in a similar way. (Order upgrade, apply upgrade file using "OS Update")
  • 2018 Offer optimising see Product Announcements, means that controllers are no longer available with XDrivers enabled, therefore the controller must be purchased, then upgraded.
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 4402
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore