How do I install termination resistors?
I/NET site
They must be installed at each end of the lan. Keep in mind that if you have a stub (tee) near what you think is the end of the lan which is very long, the stub (or what you thought was the stub) is really the end. Anyway, the resistor is installed between the signal wires. In other words, one end goes into terminal one of the controller/tap/NPR along with the positive signal wire and the other end goes in terminal 2 with the negative wire. If you have a controller lan separated by a repeater or FOIs, it should be treated as 2 lan segments and each of them terminated at the repeater or FOI as well.