How to increase the number of Modbus registers the Xenta server polls in a single request?
TAC Vista
  • XBuilder
  • Xenta 511
  • Xenta 913
  • Xenta 701
  • Xenta 711
  • Xenta 721
  • Xenta 731
This feature is not well documented in the Xenta 700 documentation, though it is mentioned in the TAC Xenta Server – Gateway, Technical Manual (Xenta 913).
  1. In XBuilder, selected the Modbus device in the network view.
  2. Under Link->Max Range Size you will see the current setting, the default is 20 which most devices support.
  3. Change the number to the desired value between 1-100. Note that the value must be supported by the device!
  4. Download the project to the device to commit changes.