Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

How to identify a WorkPlace Tech application as created/edited with version 3.2sp1 (or older) so it can be converted by WPT 4.x or WPT 5.x

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to identify a WorkPlace Tech application as created/edited with version 3.2sp1 (or older) so it can be converted by WPT 4...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • sesa116877
    sesa116877

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1260 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to identify a WorkPlace Tech application as created/edited with version 3.2sp1 (or older) so it can be converted by WPT 4.x or WPT 5.x

Picard Product_Support
‎2018-09-07 01:57 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-10-30 10:56 AM

Issue

How can a WorkPlace Tech application be identified as created/edited with version 3.2sp1 (or older) so it can be converted by WPT 4.x or WPT 5.x?

Product Line

TAC IA Series

Environment

WorkPlace Tech

Cause

Jobsite with an installed base of MNL or MNB controllers but the version of WorkPlace Tech used is not known.

Resolution

NOTE: Do not allow the application to be converted, if so prompted.

  1. Open the application file in an appropriate version of Visio. (WorkPlace Tech not needed).
  2. While holding down the left-shift key, right click on the background of the application and select "Show ShapeSheet", holding the left-shift key down until the ShapeSheet window is displayed.
  3. Verify that the text table window that is opened shows the file name followed by "". If not, close the shapesheet window and repeat step 2. The left-shift key must be held down until the ShapeSheet table is displayed.
  4. Look for the "User-defined Cells" table in the displayed information and verify that an entry named "User.wptVersion" is shown. This field will show the version of WorkPlace Tech that created the application. If either the "User-defined Cells" section or the "User.wptVersion" field are not displayed in the shape sheet, the application was created / edited with a version of Workplace Tech prior to version 3.2sp1.
  5. Close Visio. Respond by clicking NO if Visio prompts to save the document.

In Visio 2010, the ShapeSheet is located on the Developer tab, which is not displayed by default. To show the Developer tab, do the following:

  1. Click the File tab.
  2. Under Help, click Options.
  3. Click Customize Ribbon.
  4. Under Customize the Ribbon, select the Developer check box.

To open the ShapeSheet, do the following:

  • On the Developer tab, in the Shape Design group, click the arrow below Show ShapeSheet and then do one of the following:
    • To open the ShapeSheet for a selected shape, click Shape.
    • To open the ShapeSheet for the active page, click Page.
    • To open the ShapeSheet for the entire drawing, click Document.

Wptversion LL3336.jpg

 

Labels (1)
Labels:
  • TAC IA Series
Tags (5)
  • Find more articles tagged with:
  • 3336
  • shapesheet
  • tech
  • versio
  • visio
Was this article helpful? Yes No
50% helpful (1/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.