How to have a program in CyberStation detect memory loss at an Andover Continuum first generation controller (CX99xx, CX9702) and perform an automatic reload.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to have a program in CyberStation detect memory loss at an Andover Continuum first generation controller (CX99xx, CX9702)...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • AbeMeran
    AbeMeran

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2735 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to have a program in CyberStation detect memory loss at an Andover Continuum first generation controller (CX99xx, CX9702) and perform an automatic reload.

Picard Product_Support
‎2018-09-06 02:05 PM

Issue

Andover Continuum first generation controllers do not support backing up their object database to flash memory, under certain conditions these controllers can reset and lose the object database that is kept in RAM memory.

Environment

CyberStation

CX9200

CX9900

CX9940

CX9400

CX9702

Cause

Controller memory loss due to reset.

Power failure that lasts beyond the capacity of the battery to retain memory.

Resolution

The following sample program running in the CyberStation monitors a controller for memory loss and automatically performs a reload (Send to controller), optionally the program can trigger an alarm to announce the memory loss and reload event.

Note that the cause of a controller reset should never be ignored and must always be investigated thus the automatic reload program is not intended as a fix for a reset issue.

SAMPLE PROGRAM

'This program monitors a CX99xx controller and reloads it if a memory loss is detected.

'The program is triggered by the Minute system variable

'CONFIGURATION

'Flow type:      Looping

'Auto start:      False

'CX9900.11.Reload is an analog value point in CyberStation attached to an alarm so that 'a memory loss/reload event can be announced.

CheckCommStatus:

'Make sure controller is online before attempting to communicate with it

  If LocalNetwork\CX9900.11 CommStatus = OffLine then Stop  Else Goto CheckController

CheckController:

'If controller memory loss detected, reload the controller

  If LocalNetwork\CX9900.11\Freemem > 5600000 then 'replace 5600000 with appropriate value for your particular controller

    CX9900.11.Reload = 1 'Send alarm to announce memory loss/reload event

    Reload LocalNetwork\CX9900.11

    Goto WaitForReload

  Else

    Stop

  Endif

WaitForReload:

'Wait here to avoid getting into a reload loop

  If LocalNetwork\CX9900.11 Reloading = False or TM > 15 then

    CX9900.11.Reload = 0

    Stop

  Endif

E:

'If an error is detected stop the program, we'll try again next time the program is triggered

'NOTE we will end up here if the controller is actually offline but CyberStation has it as

'Online due to probe time latency

  Stop

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 4713
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of