How to get SQL Server 2005 to work with a Niagara G3 Enterprise Network Server.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to get SQL Server 2005 to work with a Niagara G3 Enterprise Network Server.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • sesa119747
    sesa119747
  • DavidFisher
    DavidFisher

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1605 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to get SQL Server 2005 to work with a Niagara G3 Enterprise Network Server.

Picard Product_Support
‎2018-09-07 01:25 AM

Issue

How to get SQL Server 2005 to work with a Niagara G3 Enterprise Network Server.

Environment

  • Niagara G3 Enterprise Network Server
  • SQL Server 2005

Cause

The SQL Server need to enable TCP/IP and open TCP port number 1433.

Resolution

"...To get SQL Server 2005 Express (the free edition) configured properly simply follow these steps...

  1. Download SQL Server 2005 Express Edition here.
  2. Download the SQL Server Management Studio Express from the above URL (note: advanced services are not needed). This is optional but it does provide a useful interface for running SQL queries if desired.
  3. Before installing SQL Server 2005 Express Edition, ensure the user is logged on with administrative access to the PC and all older versions of SQL Server are uninstalled.
  4. When installing SQL Server 2005, ensure mixed mode is enabled and the give 'sa' user a strong password.
  5. Once installed, open the SQL Server Configuration Manager ('Start', 'Programs', 'Microsoft SQL Server 2005', 'Configuration Tools', 'SQL Server Configuration Manager').
  6. Once the Configuration Manager has been opened, enable TCP/IP so G3 can connect to SQL Server (by default this is switched off).
  7. Using the tree, navigate to 'SQL Server 2005 Network Configuration' and then 'Protocols for SQLEXPRESS'.
  8. Right click TCP/IP and select 'Properties'. The TCP/IP Properties window should now appear.
  9. On the first tab labeled 'Protocol', ensure the 'Enabled' property is set to 'Yes'.
  10. Go to the second tab labeled 'IP Addresses'.
  11. In the section labeled 'IPAll' delete any entry in 'IP Dynamic Ports' and enter the value 1433 in 'TCP Port'. Once completed click ok.  Note that the default port is a 5-digit number that will NOT work.  It must be removed.
  12. Restart the SQL Server Express service. If it can't be located easily in Windows, then reboot the computer.
  13. Niagara G3 should now be able to connect to SQL Server 2005. Before attempting to connect, ensure all firewalls are properly configured so the connection can be made.
  14. If running the Enterprise Network Server on a different computer, then open up a Windows command prompt on the ENS computer and type 'telnet yourIPAddressGoesHere 1433'. If the command prompt window goes blank then connections can be made to this IP address and port number.
  15. Open Workbench and run up the desired station.
  16. Ensure the station is licensed to use the rdbSqlServer feature.
  17. Add the 'RdbmsNetwork' component to the server station.
  18. Add the 'SqlServerDatabase' component.
  19. Configure the properties for the 'SqlServerDatabase' component.
  20. Type in the IP address, port number (1433 in this example), user name and password for the connection.
  21. Ping the 'SqlServerDatabase' and ensure its status is 'ok'.
  22. Export historical data to the Sql Server database by adding a new 'SqlServerHistoryExport' component and setting up its 'History id' property to point to an existing history already in the station".

Ensure Niagara G3 version 3.0.100 and above is used in order for the connection to work.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 2727
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore