How to export histories from a Niagara G3 ENC to a Niagara G3 Enterprise Network Server (ENS)
  • How to export histories from a Niagara G3 ENC to a Niagara G3 Enterprise Network Server (ENS)
  • sesa116871
    sesa116871
‎2018-09-06 02:36 PM
I/A Series G3 (Niagara) ENC and Enterprise Network Server (ENS).
Technical tip.
To export a history to the ENS,
  1. expand the ENC's Niagara network and locate the ENS station.
  2. Expand the station, right-click Histories, and choose "View > Niagara History Export Manager"
  3. Click the "Discover" button to discover the histories in the ENC station. Highlight the desired histories, and click the "Add" button. Select the desired Execution Time (Daily, Manual, Interval), set the "Enabled" field to True, then click OK.
  4. Send initial history data to the ENS by clicking on the "Archive" button.
  5. In the Nav tree, open the ENS station. Expand the server's History folder. Verify that the histories from the ENC station are there.
  • TAC IA Series