How to display the date as an object in Sigma.
  • How to display the date as an object in Sigma.
  • DavidChild
    DavidChild
‎2018-09-06 11:13 AM
BAS
SIGMA
For Day and Month only, the following programmable point needs to be configured:
10 XFlo = FLOAT ( MONTH )
20 XFlo = XFlo / 100.000
30 YFlo = FLOAT ( DAY )
40 RETURN VIA TEXT 449 VALUE XFlo + YFlo
The date will be displayed in the dd.mm format.
Shorttext will need to be created as below:
%2.2f and will be displayed as 17.07
or
Date:%2.2f and will be displayed as Date:17.07
If Day, Month and Year is required the following can be configured:
20 XFlo = XFlo * 100.000
40 YFlo = YFlo * 10000.0
50 ZFlo = FLOAT ( YEAR )
60 RETURN VIA TEXT 449 VALUE XFlo + YFlo + ZFlo
The date will be displayed in the ddmmyy format.
Date:%2.0f and will be displayed as Date:170712
  • Satchwell BAS & Sigma
  • 10867
100% helpful (1/1)