How to display a check list or report when a specific alarm becomes active.
  • How to display a check list or report when a specific alarm becomes active.
  • AbeMeran
    AbeMeran
‎2018-09-06 01:42 PM
PE programming required to display a check list doc, report etc on specific alarm link of an object such as a door.
Continuum provides built in functionality to run a program when any of the 8 alarms associated with an object goes into alarm. In order to execute some actions on a specific alarm some PE programming is required.
This article provides sample User Defined PE Alarm function to display a particular document depending on which of the alarm links associated with a door object is active.
Not known cause
  1. Configure the Cyberstation that will be displaying the doc, report etc for User-Defined Alarm Function (See Cyberstation online help for instructions on how to do the configuration).
  2. In the PEAlmFunction use code to qualify the alarm and display the doc or report that applies to the particular alarm type.
-- SAMPLE CODE
Arg 11 AlarmENROLL
Arg 12 EventNOTIF
if EventNOTIF is not "DoorAlarm" then return 'Only looking for door alarms in this example.
if AlarmENROLL = "Door Forced Open" then SHELL "C:\Temp\CheckListForDoorForcedOpen.doc"
if AlarmENROLL = "Door Ajar" then SHELL "C:\Temp\CheckListProcedureForDoorAjar.doc"
-- END SAMPLE CODE
NOTE: The alarm function will be invoked every time any alarm comes in; in the example above all door alarms have been associated with the same EventNotification (DoorAlarm) in order to make sure the function can execute only when door alarms are reported.