How to disable HTTP in Security Expert SOAP web service and Web Client

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to disable HTTP in Security Expert SOAP web service and Web Client
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Mahmoud_Sayed
    Mahmoud_Sayed

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5133 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to disable HTTP in Security Expert SOAP web service and Web Client

Kirk Mahmoud_Sayed Kirk
‎2024-02-21 03:48 PM

on ‎2024-02-21 03:48 PM

Issue

Need to disable HTTP access for both SOAP web service and Web Client to allow HTTPS access only.

Product Line

EcoStruxure Security Expert

Environment

  • Security Expert Server
  • Security Expert SOAP Web Service
  • Security Expert Web Client

Cause

Need to disable HTTP access for enhanced cybersecurity

Resolution

Disable HTTP access for SOAP:

  1. Navigate to the SOAP IIS Directory, by default this is "C:\inetpub\wwwroot\SecurityExpertSOAPService" and open the "Web.config" file using a text editor such as Notepad or Notepad++.
  2. Scroll down to the <services> section and comment out the following two lines:
    1.  <endpoint address="" binding="basicHttpBinding" bindingConfiguration="basicHttpEndpointBinding" contract="GXWCF2.IService1" />
    2. <endpoint address="mex" binding="mexHttpBinding" contract="IMetadataExchange" />
      
      SOAP WebConfig diable HTTP 1.jpg

       

  3. To confirm that the HTTPS version of the service is accessible, paste the following link into
    the URL bar and replace the placeholders with the relevant values: https://<pcname>.<domainname>:<portnumber>/SecurityExpertSOAPService/service.svc. A web page will open with a message saying that the service has been created, this confirms SOAP is working correctly.

Disable HTTP access for Web Client:

  1. Open Internet Information Server (IIS) manager. 
  2. Right click on the SecurityExpertWeb site and select "Edit Bindings".IIS Edit bindings.jpg

     

  3. Remove the HTTP site binding.Remove Binding.jpg

Configure Web Client to connect to SOAP via HTTPs:

  1. Navigate to the IIS directory for the Web Client, by default this is "C:\inetpub\wwwroot\SecurityExpertWebClient". Go to the 'include' directory and open the file 'soap.connect.php"
  2. Modify the address on the $wsdl = to the HTTPS SOAP address, and change the port number as well. Additionally, 'localhost' does not work, and it must be changed to hostname with qualified domain name. See below image for reference:

web client config.jpgOnce this change is made it should now be possible to browse to the web client over HTTPS.

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • MahmoudSayed24
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore