Steps to connect a 4-20mA or 0-20mA sensor to a Universal Input

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Steps to connect a 4-20mA or 0-20mA sensor to a Universal Input
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Ramaaly
    Ramaaly

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
7215 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Steps to connect a 4-20mA or 0-20mA sensor to a Universal Input

Picard Product_Support
‎2018-09-07 06:01 AM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2025-09-03 11:08 AM

Issue

Current transducers require an additional external resistor fitting to a Universal input to read the current flow, what resistor and input point settings are required?

Product Line

Andover Continuum

Environment

  • All controller with Universal Inputs (both 5V and 10V).
  • 4-20 mA

Cause

There is a requirement to define the resistor value to be connected across the input, also the settings for the upper and lower voltage in the input point configuration.

Resolution

Download the attached Current Inputs.PDF file, although this was originally written for Infinity controllers it is fully applicable for i2 and b3 controllers. Controllers like the i2/b3920, i2/b3810 have 10V inputs other i2/b3 controllers have 5.12V inputs, check the product datasheet specification if you are unsure.

The file details the value of the resistor to use in the circuit and the upper and lower voltage settings to enter in the Auto Conversion box in the input point, these will correspond to the sensor reading at 0mA and 20mA, or 4mA and 20mA depending on your sensor output.

For controllers that allow the pull up resistor to be switched out, ensure that it is in circuit for these setting to work correctly.

The UI-8-10-10V I/O Modules should be set to 0-5V input with the reference resistor On, then setup as per all other 5.12V input controllers.

Note: The part numbers listed for the resistors are no longer available through Order Entry and should be sourced from your local stockist.

Link to file:

Current Input ISM.pdf

 

Suitable component resistors:

For 10V inputs: RS 165-472

For 5V inputs: RS 165-185

0

Labels (1)
Labels:
  • Andover Continuum
Attachments
Tags (2)
  • Find more articles tagged with:
  • 4450
  • RamaAly25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore