Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

How to configure a TAC Xenta server in Lonmaker when also being used as the communication port in TAC Vista

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to configure a TAC Xenta server in Lonmaker when also being used as the communication port in TAC Vista
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa150555
    sesa150555
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1716 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to configure a TAC Xenta server in Lonmaker when also being used as the communication port in TAC Vista

Picard Product_Support
‎2018-09-06 12:03 PM

Issue

How to configure a TAC Xenta server in Lonmaker when also being used as the communication port in TAC Vista

Environment

TAC Vista

Lonmaker

TAC Xbuilder

TAC System plug-in

Cause

Needs to use the Xenta Server as a lonworks device and the Network Interface in TAC Vista.

Resolution

Using Xenta Server 7xx and LonMaker

 

  1. Create the Xbuilder project using “stand alone Xbuilder”
    1. Add the IO modules that the Xenta Server is using and assign neuron Ids
    2. Create the SNVTs for the Xenta Server.
    3. Send the project to target.
       
  2. Create LonMaker and TAC Vista database
    1. Create you LonMaker database, register the necessary plug- ins. TAC System plug- in and TAC Device plug- in are used for the Xenta Server.
    2. Add the nodes on you Network including the Xenta Server but not the IO modules. You can use a generic template for the Xenta Server and browse in the XIF file.
    3. Open system plug-in. Right click on The Xenta server and select “Configure…”. Browse in the Xbuilder project. Click on the “add and mach IO”. Click ok.
    4. Go to TAC Network – Settings, Set the Vista communication port to the correct Xenta server type. Also select if you want the IO modules to be commissioned in LNS. Click Ok


       
    5. Still in the system plug in right click on the Xenta Server and select “set as network interface”.
    6. Update TAC Network. Start the server and update TAC Vista Database form the system plug in. Create group bindings if you have any Xenta 401, 30x, 28x controllers.
    7. Close the system plug in.
    8. Resynchronize the drawing to database. Commission devices. Create bindings.
    9. Open TAC Vista workstation, right click and edit the Xenta server (This can also be done form the system plug in configure command). Send the project to target.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 11217
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of