How to calculate the pressure drop across a fully open valve
  • How to calculate the pressure drop across a fully open valve
  • DavidChild
    DavidChild
‎2018-09-06 10:51 AM
Valves
End user wants to calculate the pressure drop across a  valve for a given flow rate.
1. Select a valve to suit the application and note its Kvs. note if the figure is Cvs then Cvs * 1.03 = Kvs
2. Flow rate is required.
P (bar) = (m3/hr / Kvs) squared.
or
P (bar) = ( (l/s * 3600 /1000) / Kvs) squared.
To convert to Bar to Kpa:  1 Bar = 100 Kpa
  • Field Devices
  • 11888